Testing power monitor with 1 CT on 1 wire of a dryer cord #146

Answered by David00
acabrera2012 asked this question in Q&A
Discussion options

You must be logged in to vote

Everything looks correct from what I can see. I think it must be that the CT you're using is spec'd differently than the ones from my shop. That's okay, as long as the output from the CT doesn't overload the input of the power monitor, and based on the raw data plot, it's not. (It looks like the CT1 data peaks around 850 or so which is perfectly fine. because the limit is 1023).

You'll just have to update the calibration value for the channel to get the measurements to align with a handheld AC clamp meter. If they're currently 10x what you are expecting, start with a calibration value of 0.10 for CT1. Keep in mind you don't have to guess about the calibration value - the docs show a way t…

Replies: 1 comment 4 replies

Comment options

You must be logged in to vote
4 replies
@acabrera2012
Comment options

@David00
Comment options

Answer selected by acabrera2012
@acabrera2012
Comment options

@David00
Comment options