Replies: 5 comments 11 replies
-
Same on my end. |
Beta Was this translation helpful? Give feedback.
-
Hi CircutSetup - thanks for your input.
Well in my case there is NOTHING plugged in the CT sockets. So definitely no current is flowing (other that maybe induced on the PCB?). I clearly see a big difference in those offsets between the main board and the expansion boards. |
Beta Was this translation helpful? Give feedback.
-
I think we have identified the root cause for the calibration offsets. See #88 (comment). |
Beta Was this translation helpful? Give feedback.
-
Jut wanted to say THANK YOU for resolving this issue. I finally found some hobby time to put everything together. Things work great, I did not need to run the manual calibration on my meter as the offsets were really negligible. |
Beta Was this translation helpful? Give feedback.
-
I am in the process of calibrating my current transformers. (a pair of 200A/50mA SCT-024 and some 100A/50ma SCT-013-000)
Using a resistive load drawing about 7 Amps, I can easily adjust the individual transformer 'gain_ct' factors to match the reading from my Fluke current clamp. So far, so good.
But when shutting down the resistive load while still keeping the current transformers in-place, so with zero Amp flowing through the circuit, the 6 Channel main board is still reporting some small current and power values, like 0.14A for the current, and a few hundredth of Watt for the power. I would expect to read 0 Amps in that case. I guess I am rather hitting the measurement precision of the ATM90E32 chips?
I tried to compensate for those tiny offsets using an esphome filter offset, but it is like chasing a moving target, the current and power offsets remains tiny, but I cannot compensate for them completely.
Any comments would be appreciated.
Beta Was this translation helpful? Give feedback.